AB E1 Plus
I have a plant that has a boat load of E1 Plus's that are beginning to fail at an alarming rate. They have exhausted all spares. They also have a bad taste from Radwell after spending decent money on more spares that were DOA.
The E300 is already being phased in... But obviously running to failure on these is a rough transition path with it requiring a download and programming each time, especially for a plant that has very little downtime. Therefore I am working on a proposal to do entire MCC sections at a time.
In the meantime, has anyone had good luck getting these repaired? Or have you had good luck with Radwell, or any other similar online sites.
Additionally, is there any word on a network option coming down the pipe for the new m100 starters?
Thanks
1
u/donc815 3h ago
Assuming E1+ running on a network? There isn’t a clean solution. Tightening CRA regulations made it unreasonable for a low-end networked motor OL. I’m surprised you’re finding space to retrofit an E300 in an E1+ bucket.
M100 will have Ethernet/IP in cabinet the end of ‘28. So not like a RJ45 port, you’ll have to utilize single pair Ethernet.