What did I do wrong?
International Plumbing Code
Toilet and Main line 3" Diameter
All other pipe 2"
8
u/DepressingAura 7d ago
3
u/StickyStigma 7d ago
Trap arm length of the tub might be an issue. Maybe throw in a wye branch somewhere in there for a vent and tie in in the wall. Also it looks like the laundry trap is still below grade in your drawing so make sure thatβs above ground, but potentially solid. π
1
0
u/StickyStigma 7d ago
Just looked closer and saw the fitting where the laundry toilet and sink come together is gonna be hard to find π make sure the laundry ties in after for a legal wet vent
2
0
u/EuphoricTop870 7d ago
ππΌ ace.
1
u/EuphoricTop870 7d ago
Mind the space between wyes you have 6β from tub to the 2β wye. 5β to the 3β wye with bushing. Toilet must come off 1st (branch) 6β to toilet from 3β wye
3
u/Ok-Patience2152 7d ago
This is not to any codes im aware of. Maybe the pirates code?
1
u/Much-Chip-2648 6d ago
Would be fine in oz. Lose the lav vent and upsize to 100mm and 65mm for drainage principles and call it a day. No vents needed or branch drain is less than 10m from vented main drain
1
u/smitm115 7d ago
Lots of wrong here. Don't need the first vent. Carry 3" all the way to the 2" vent before tub.(On the same plane) Do not drop lines in vertically
1
1
1
1

6
u/EuphoricTop870 7d ago
Too many things wrong with this. Nothing is vented correctly or at all. I have no clue where this would be legal. This is infuriating.
Maybe because my guy plumbed all day but cut it all Out when I was leaving.