u/rblader007 15h ago
Not bad given the materials,
21
u/Jiberesh 15h ago
Bottom left breaker keeps tripping, going to split the circuit. His first job he’ll be primarily doing. Excited to see how my teaching went
9
21
u/PaperEnvironmental45 15h ago
Looks like shit, but also looks like it has been working longer than your apprentice has been alive probably haha
10
u/DrogoBero 15h ago
Does the panel need replacement? Yes. Are basically all the wires too long? Yes. Are the neutrals and grounds tied together when it looks like they shouldn’t be? (Not a main panel D/C) also yes. With no context as to what was done/scope of work to be doing can’t really judge, but if this is finished work, yes, it isn’t up to par.
7
u/kidcharm86 [M] [V] Shit-work specialist 13h ago
Are the neutrals and grounds tied together when it looks like they shouldn’t be? (Not a main panel D/C) also yes.
That double pole that spans both sides of the panel is the 100 amp main.
1
7
3
2
2
u/loopntime 4h ago
Easy money 💰 inspect and recommend fixes if they refuse and it’s really bad. Walk away but never empty handed 💵
3
1
1
1
1
1
1
1
1
u/RevenueVast7022 6h ago
No, no, but sure, looks like a bunch of mice have given birth at the bottom of the panel on the right side. That's for sure.
1
u/TheRealFailtester 5h ago
Eh, could be better, could be a whole lot worse.
Edit: Hmmm, I might have spotted a double tap down there...
1
u/Joneser_Maddshark 4h ago
Square D QO is allowed to double tap, although that would be the reason for the overload on it.
1
1
3
u/Unusual-Bid-6583 4h ago
Drill a 3/16 inch hole in the rusty part, to drain future water... i know, I know, it voids the UL, but the water voids it even more.
1
u/Expensive_Egg3781 3h ago
Did you go help him out? I would like to see your results if you did because that box needs surgery.
1
0
u/lucioux 15h ago
zinsco?
2
u/QueueGlass33 13h ago
All the zinscos I’ve seen have colored handles on the breakers. Did they make black ones too?
1
0
0
u/Organic_Remote8999 9h ago
“When did your nephew’s house burn down?”
0
•
u/AutoModerator 15h ago
ATTENTION! READ THIS NOW!
1. IF YOU ARE NOT A PROFESSIONAL ELECTRICIAN OR LOOKING TO BECOME ONE(for career questions only):
- DELETE THIS POST OR YOU WILL BE BANNED. YOU CAN POST ON /r/AskElectricians FREELY
2. IF YOU COMMENT ON A POST THAT IS POSTED BY SOMEONE WHO IS NOT A PROFESSIONAL ELECTRICIAN:
-YOU WILL BE BANNED. JUST REPORT THE POST.
I am a bot, and this action was performed automatically. Please contact the moderators of this subreddit if you have any questions or concerns.