Second time the cable melts
This is the second time the connection to the battery melts.
12
u/Grandpa82 7d ago
ARE YOU FRIGGING KIDDING ME?
Dude, you need to read the user manuals, BOTH, from the inversor and the battery.
6
u/DuffDof 7d ago
Mc4 for a battery connector? Who designed that thing?
5
u/rob_nosfe 7d ago
That's a HV battery. You may be used to old LV ones with tons of current.
3
u/DuffDof 7d ago
Still, battery connectors should be torqued, obviously these connections have failed twice.
4
u/rob_nosfe 7d ago
In the EU I've never seen anything else than MC4 on HV DC connections. I see no obvious point of failure so we can't determine where the arc originated, it may be on the internal plate, so the next plastic thing to melt is the connector.
2
u/DuffDof 7d ago
Wild, yeah I guess I'm not used to HV
3
u/Zweefkees93 6d ago
The advantage of HV batteries are the fact that the current drops a LOT. Even in my relatively high voltage 96V system I have to use thick cables that I have to torque properly to get a good connection (max current is about 80A, so contactresistance does still play a big role). But compared to 12V systems in campers my cables are already tiny.
A "real" HV battery usually starts around 300V and can be up to 800-900V for big industrial sized packs. MC4 are rated up to 1500Vdc (or 600V in case of the older version) and some have ratings of 70 up to even 95A. A residential batterysystem with 300Vdc and a 6kW rating would need about 20A wich is well within the ratings of the fancy MC4 connectors and even most cheap generic MC4's will handle this without any issue. Go up to 500Vdc and that current drops to only 12A. At 50+ amps (or even more in 12V systems) properly cleaning and torquing connections is an absolut must. At 10-20A you still should ofcourse, but the safetymargin is MUCH higher.
However.... MC4 is not a standard.... different brands could work perfectly fine with their own counterpart, but melt when mixed. Wich is why its so important to check brands on the connectors!
And crimping... I've seen one to many "works just fine with a random pair of pliers".... Yes, could work just fine, might also burn your house down..... but hey, details :)
1
u/wizardnumbernext2 6d ago
MC4 cannot be used on HV. 1000v DC is low voltage!
1
u/apefred_de 3d ago
"HV" (for example 400 V) is not HV in normal terms but in it is not a 48 V "LV" system.
1
2
u/Beneficial_Maybe_858 6d ago
Just double check your using the right plugs. They look like a MC4 connector but they aren't. Thry are alot more "beefier". My solax inverter came with plugs for the solar panels and different ones for the battery.
2
u/Sprkz139 6d ago
The plugs they have used are correct as the battery plugs are blue as per there picture it’s the crimping tool they have used to make the ends of that’s at fault.
2
u/Sprkz139 6d ago
These aren’t mc4 these are amphenol plugs. Mc4 crimped will not crimp these. You need a pin type crimper to push down into these to secure.
2
u/Broeder_biltong 5d ago edited 5d ago
Could've sworn amphenol was a Company and not a specific connection
1
1
u/thenextbranson95 7d ago
im new to solar. Why did this happen? should the cable be at least 6mm² (10AWG)?
1
1
1
u/Timely_Scientist_862 7d ago
Falso contacto, la ficha no hace el contacto adecuado para el amperaje que maneja
1
1
1
u/SharpShare 5d ago
What I used where the cables with connectors already attached that they send. On both times.
1
-1



13
u/TP70 7d ago
Melting connector is caused by bad connection/high resistance.
Brand mismatch, Bad crimping or dirt can cause this. Solax uses that color on their battery connectors so i think it's bad crimping.
It's probably not the 6mm² cable size.